What is method or procedure for making 1 hour and 2 hour fire rating walls?
Do you need to remove the ads? Become VIP Member
Join TheConstructor to ask questions, answer questions, write articles, and connect with other people. When you join you get additional benefits.
Log in to TheConstructor to ask questions, answer people’s questions, write articles & connect with other people. When you join you get additional benefits.
Lost your password? Please enter your email address. You will receive a link and will create a new password via email.
AdityaBhandakkar
Values for fire-resisting walls are provided in ACI 216.1-07 ratings in between 1 to 4 hours. Please go through it for details.
ACI 216.1 -07 describes rating for 1hour, 1.5 hours, 2 hours, 4 hours.
You can also refer IS 3089:1979 for values of fire-resisting for a different structure and dimensions.
Komal Bhandakkar
Making of 1hr and 2hr firing wall:
This is one of the most popular questions.
Basically, building codes typically require that the structure is wall roof floor, the roof is fire-resistant.
The standards set forth by the International Building Code (IBC). fire resistant Wallis designed for a definite time period.
According to ‘Commercial drafting and detailing book’, a one of our fire rated wall consists 2 x 4 studs spaced 16 inches from the centre of one stud to the centre of the next.
Madeh Izat Hamakareem
According to ACI 216.1-07 (Code Requirements for Determining Fire Resistance of Concrete and Masonry Construction Assemblies), the thickness of plain and reinforced concrete bearing or nonbearing walls required to provide fire-resistance ratings of 1 to 4 hours, shall comply with the minimum equivalent thickness values provided in Table below:
Table 1 fire resistance rating of single layer concrete walls
Aggregate
type Minimum equivalent thickness for fire-resistance rating, in.
1 hour 1.5 hours 2 hours 4 hours 4 hours
Siliceous 3.5 4.3 5 6.2 7
Carbonate 3.2 4 4.6 5.7 6.6
Semi lightweight 2.7 3.3 3.8 4.6 5.4
Lightweight 2.5 3.1 3.6 4.4 5.1
sanjaylimbasia
Dear Madeh
Greetings. Thanks for your reply. Kindly also let me know if i have to make fire rating wall with
solid or hollow blocks what is procedure.
Regards
Sanjay Limbasia
Madeh Izat Hamakareem
Dear Sanjay Limbasia
Chapter 3 of ACI 216.1-07 (Code Requirements for Determining Fire Resistance of Concrete and Masonry Construction Assemblies) provides adequate data and procedure regarding to request.
Best Regards